Hello, I am installing a boiler wood on my fuel system, I still have the connection to make and I would like to have your opinion on my schema,
thank you in advance
edited by Christophe: use our host of images stp.
The subject has already mentioned several times, have you done a research?
For example here is my montage wood: https://www.econologie.com/forums/installati ... t3494.html
Your diagram is inspired by http://pagesperso-orange.fr/herve.silve/schemasbois.htm
boiler coupling wood and oil: map and diagram
Hi Letitus,
To secure the installation you need a cooling coil (integrated) or a cold water injection system at the boiler inlet (with thermal valve)
In addition you intend to operate without buffer tank, which is not ideal to optimize the use of this boiler.
There is a circulator for the wood boiler alone, but no recirculation loop with heat valve. There is a high risk of boring, at least at the beginning of operation.
In your diagram, nothing prevents the water heated by the wood boiler from circulating in the oil boiler and vice versa.
There are 2 check valves, 1 alone would suffice.
Your schema is drawn from an existing schema, but more complete. It's a bit normal that there are inconsistencies if you remove some of the elements.
A+
To secure the installation you need a cooling coil (integrated) or a cold water injection system at the boiler inlet (with thermal valve)
In addition you intend to operate without buffer tank, which is not ideal to optimize the use of this boiler.
There is a circulator for the wood boiler alone, but no recirculation loop with heat valve. There is a high risk of boring, at least at the beginning of operation.
In your diagram, nothing prevents the water heated by the wood boiler from circulating in the oil boiler and vice versa.
There are 2 check valves, 1 alone would suffice.
Your schema is drawn from an existing schema, but more complete. It's a bit normal that there are inconsistencies if you remove some of the elements.
A+
0 x
Yes indeed I took again the drawings ^ ^ I wanted to establish the installs like that which I have at this moment (without the wood property)
I have the idea to put a balloon buffer but limited at this time nv finance, I think to install it from here 2ans
the goal is that I would like to heat my fuel fireplace (the production of hot water is integrated)
(but no recirculation loop with thermal valve)
what's this?
I have the idea to put a balloon buffer but limited at this time nv finance, I think to install it from here 2ans
the goal is that I would like to heat my fuel fireplace (the production of hot water is integrated)
(but no recirculation loop with thermal valve)
what's this?
0 x
Bonjour,
Here is an example of a connection
So actually if you want to maintain the heating body of your oil boiler at temperature (for DHW), it is necessary to connect the wood boiler in series on the return and the bypass when it does not work thanks to the mains valve A / B.
Attention, keep the boiler oil temperature causes losses if it is placed in an outdoor room (the losses do not heat the house)
You can automate the passage A / B by choosing a motorized valve that switches to B if the wood boiler works (easy, it is the same command as its circulator). Otherwise, the valve must switch to A.
To test the buffer balloon formula without investing a lot, you can take one (or more) used hot water balloons. We find less than 100 euros for 300L.
I have one of my contact who tried, he is happy, even if he knows that the capacity is a bit fair (we can always add some later)
For the heat valve and the recirculation loop, the objective is to operate the boiler with a minimum temperature.
An automatic opening valve (usually 55 ° or 65 ° C) is required.
In your case, the utility of this system depends on the power of the boiler and the rate of rise in temperature of your installation.
Everything is explained here
http://pagesperso-orange.fr/herve.silve/bois.htm
A+
Here is an example of a connection
So actually if you want to maintain the heating body of your oil boiler at temperature (for DHW), it is necessary to connect the wood boiler in series on the return and the bypass when it does not work thanks to the mains valve A / B.
Attention, keep the boiler oil temperature causes losses if it is placed in an outdoor room (the losses do not heat the house)
You can automate the passage A / B by choosing a motorized valve that switches to B if the wood boiler works (easy, it is the same command as its circulator). Otherwise, the valve must switch to A.
To test the buffer balloon formula without investing a lot, you can take one (or more) used hot water balloons. We find less than 100 euros for 300L.
I have one of my contact who tried, he is happy, even if he knows that the capacity is a bit fair (we can always add some later)
For the heat valve and the recirculation loop, the objective is to operate the boiler with a minimum temperature.
An automatic opening valve (usually 55 ° or 65 ° C) is required.
In your case, the utility of this system depends on the power of the boiler and the rate of rise in temperature of your installation.
Everything is explained here
http://pagesperso-orange.fr/herve.silve/bois.htm
A+
0 x
thank you for your help
the AB valve is a motorized mixing valve?
with the information of the aquastat she switches to position wood and fuel if the wood is not en route?
I would like the fuel boiler to start automatically when the wood does not heat up any more, AB's motorization is the best not?
only one vase of expension suffices?
if my AB valve does not work (failure), will my valve protect the installation?
I am painful huh
thanks again
the AB valve is a motorized mixing valve?
with the information of the aquastat she switches to position wood and fuel if the wood is not en route?
I would like the fuel boiler to start automatically when the wood does not heat up any more, AB's motorization is the best not?
only one vase of expension suffices?
if my AB valve does not work (failure), will my valve protect the installation?
I am painful huh
thanks again
0 x
-
- Moderator
- posts: 79374
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11064
You have to be able to work independently with wood or not?
If yes the proposed 2 scheme are to be reviewed because the wood will heat the oil boiler.
Question: on the 1st diagram, pkoi you put 2 "10" valves on the wood circuit?
If yes the proposed 2 scheme are to be reviewed because the wood will heat the oil boiler.
Question: on the 1st diagram, pkoi you put 2 "10" valves on the wood circuit?
0 x
Do a image search or an text search - Netiquette of forum
-
- Moderator
- posts: 79374
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11064
Ok so you will NEVER heat 100% with wood? Where is the DHW tank? "In" the oil boiler?
For the flaps they duplicate: one will be enough.
For the flaps they duplicate: one will be enough.
0 x
Do a image search or an text search - Netiquette of forum
no wood is just a booster when I'm at home to relieve my consumption of fuel oil, I wish to heat the max with wood but not 100%
for the ecs I did not represent it because my boiler fuel has two separate circuit, one for the heating and the other the ecs (the boiler is a buderus logano GC115 with preparer
for the ecs I did not represent it because my boiler fuel has two separate circuit, one for the heating and the other the ecs (the boiler is a buderus logano GC115 with preparer
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 18 Replies
- 4536 views
-
Last message by francky67
View the latest post
13/02/23, 11:40A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 1 Replies
- 2175 views
-
Last message by phil59
View the latest post
31/10/22, 01:31A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 10 Replies
- 6876 views
-
Last message by Philippe Schutt
View the latest post
08/01/22, 17:22A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 1 Replies
- 13652 views
-
Last message by F Moreau
View the latest post
05/11/17, 16:27A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 2 Replies
- 10937 views
-
Last message by loop
View the latest post
22/10/13, 13:09A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : No registered users and 190 guests