Hello,
I have problems with my electrical panel.
I have a subscription to 18KW with 30A on my circuit breaker.
It is an installation from 20 years ago and the former owner with a carpenter's woodworking machine ... hence this three-phase
I balanced the phases and added RCDs that were missing from the installation.
As soon as I use the electric balloon or my new oven (it worked with the old one), the main circuit breaker 500 mA set to 30A ... blows.
The balloon was not grounded, I put it.
I tested the amperage on the phases and I am just above 16A when it jumps. I also have 16A on neutral at that time.
Where is the problem ? I no longer know where to look.
Thanks for your help ... my last hope before calling an electrician.
switchboard problem in phase - that jumps
- elephant
- Econologue expert
- posts: 6646
- Registration: 28/07/06, 21:25
- Location: Charleroi, center of the world ....
- x 7
Well, apparently you have already had the experience of lowering all the divisional units, then raising them 1 to 1, since you have come to the first conclusions.
Need refining: disconnect the devices then put them back on the circuit. Optionally, with an extension cable, fetch the current on another circuit.
If it continues under these circumstances, there is no photo: there is a fault in the insulation in your devices.
Need refining: disconnect the devices then put them back on the circuit. Optionally, with an extension cable, fetch the current on another circuit.
If it continues under these circumstances, there is no photo: there is a fault in the insulation in your devices.
0 x
elephant Supreme Honorary éconologue PCQ ..... I'm too cautious, not rich enough and too lazy to really save the CO2! http://www.caroloo.be
If the installation is old, it is not certain that the differentiation of the neutrals is made.
At the time, the neutral was neither protected nor cut.
For the installation well done there was simply a neutral bar at the bottom of the board from which all the neutral wires started.
In less well done installations, often a neutral wire was used for several circuits.
When we try to modernize such an installation, sometimes we have concerns ...
Now the strange thing is that only the main circuit breaker trips.
There would be an insulation problem on a device, the 30mA of the circuit concerned should react.
this is not guaranteed to 100% since I suppose that the main one is not selective, but still, it is always him who jumps and never the 30mA normally much more sensitive it is really bad luck .
At the time, the neutral was neither protected nor cut.
For the installation well done there was simply a neutral bar at the bottom of the board from which all the neutral wires started.
In less well done installations, often a neutral wire was used for several circuits.
When we try to modernize such an installation, sometimes we have concerns ...
Now the strange thing is that only the main circuit breaker trips.
There would be an insulation problem on a device, the 30mA of the circuit concerned should react.
this is not guaranteed to 100% since I suppose that the main one is not selective, but still, it is always him who jumps and never the 30mA normally much more sensitive it is really bad luck .
0 x
- Grelinette
- Econologue expert
- posts: 2007
- Registration: 27/08/08, 15:42
- Location: Provence
- x 272
At my place too there is a very old three-phase installation (40 years old! I will post a photo).
Apart from the phases which were unbalanced as and when the 4 homes were enlarged, I had 2 times failures that were difficult to identify:
1) an external outlet took the water and caused the general to trip randomly
2) more spectacular, breakdown that I also took a moment before finding: 2 mice had entered the table and had burned out between several contacts! ...
It is still unlikely that these are the same breakdowns at home ...
Apart from the phases which were unbalanced as and when the 4 homes were enlarged, I had 2 times failures that were difficult to identify:
1) an external outlet took the water and caused the general to trip randomly
2) more spectacular, breakdown that I also took a moment before finding: 2 mice had entered the table and had burned out between several contacts! ...
It is still unlikely that these are the same breakdowns at home ...
0 x
Project of the horse-drawn-hybrid - The project econology
"The search for progress does not exclude the love of tradition"
"The search for progress does not exclude the love of tradition"
You may not have thought that, for ErDF and its overhead circuit breaker, 18KW in three phase means that you have to 6KW maximum on each phase! ...
According to your diagram, the 2 phases on 3 have their sum of the maximum loadings which, precisely, can exceed 6KW:
1 phase: 7,5 + 1,5 + 2 + 0,2 + 0,1 + 0,1 + 0,3 = 11,7 KW
2 phase: 1,6 + 1 + 0,1 + 0,2 + 0,1 + 0,1 + 1 = 4,1 KW
3 phase: 3,6 + 0,5 + 0,1 + 0,1 + 0,1 + 2,4 = 6,8 KW
So you must either better distribute the loads over phases or ask to switch to single-phase (it's far from being free!)
According to your diagram, the 2 phases on 3 have their sum of the maximum loadings which, precisely, can exceed 6KW:
1 phase: 7,5 + 1,5 + 2 + 0,2 + 0,1 + 0,1 + 0,3 = 11,7 KW
2 phase: 1,6 + 1 + 0,1 + 0,2 + 0,1 + 0,1 + 1 = 4,1 KW
3 phase: 3,6 + 0,5 + 0,1 + 0,1 + 0,1 + 2,4 = 6,8 KW
So you must either better distribute the loads over phases or ask to switch to single-phase (it's far from being free!)
0 x
Corrigendum / Mail addendum 25 / 01 00: 02:
You may not have thought that, for ErDF and its overhead circuit breaker, 18KW in three phase means that you are entitled to maximum 6KW and simultaneously on each phase! ...
... ie 30 Amps maximum (to 2 or 3 amps close!) on each of them, whatever the time of day.
For the 1 phase, for example, only your induction plate at full power, all alone, is capable of saturating said phase! ...
To really see what is going on, the preferred tool to use is a Clamp that is placed at the top and around the phase to be examined.
Finally, note that eventually, it is entirely possible to turn the three-phase motor of your woodworking machine with a single phase ... Yep! ... but on condition that you do not ask too much of it ... And that is a whole different story! ... outside of the problem that you posed ...
You may not have thought that, for ErDF and its overhead circuit breaker, 18KW in three phase means that you are entitled to maximum 6KW and simultaneously on each phase! ...
... ie 30 Amps maximum (to 2 or 3 amps close!) on each of them, whatever the time of day.
For the 1 phase, for example, only your induction plate at full power, all alone, is capable of saturating said phase! ...
To really see what is going on, the preferred tool to use is a Clamp that is placed at the top and around the phase to be examined.
Finally, note that eventually, it is entirely possible to turn the three-phase motor of your woodworking machine with a single phase ... Yep! ... but on condition that you do not ask too much of it ... And that is a whole different story! ... outside of the problem that you posed ...
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 13 Replies
- 1786 views
-
Last message by gfgh64
View the latest post
18/01/24, 01:56A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 2 Replies
- 2155 views
-
Last message by bighorno
View the latest post
15/12/23, 21:55A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 0 Replies
- 1429 views
-
Last message by Bedouin
View the latest post
28/10/23, 22:10A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 83 Replies
- 16701 views
-
Last message by Pilpoill
View the latest post
05/10/23, 17:01A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 5 Replies
- 4834 views
-
Last message by Flytox
View the latest post
27/01/23, 19:39A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : No registered users and 226 guests