Oula ...
1) Owen, physics is not a "belief" well not on these forums !
A heat exchanger is not dimensioned with a ladle ... if Tigger tells you that he put 25m in 3/4 dishes 6m if it amuses you and you will see the results ...
2) The dimensioning of an exchanger depends on 3 main parameters (in addition to others that I neglect):
a) the exchange surface
b) the difference in T ° between the 2 "fluids" (I put "" because the fluid can be a solid, the air is a gas but which can be considered as a fluid in the heat exchanges),
c) the conductivity of the material used (copper generally but also aluminum)
3) Martian no ...
The volume of 25m by 22mm is ridiculous:
section: 2.2² * 3.14 / 4 = 3,8 cm²
length: 2500cm
Total volume: 3,8 * 2500/1000 = 9.5 L ...
Or less than 1% of the volume of the buffer ...
At the surface level this exchanger at: 2,2 * 3,14 * 2500 = 17270 cm² or 1,73 m².
In addition you are doubly wrong because this volume of water contained in the exchanger when the circulator does not turn ... also contributes to thermal storage!
4) The plate heat exchanger is not a good solution in my opinion because it requires the management of a 2nd circuit with, at least, a circulator to manage ... short + complicated = + trouble ...
5) I will search some dimensioning formulas but basically you can compare the area needed to that of a 5kW aluminum radiator .... With a known delta, say, 40 ° C, these formulas will allow you to know which exchange surface you need.
But you should know that in heat exchange it is like driving: the theory has its limits and it only allows to have an idea of reality (but the theory of heat transfers sticks more to reality than that motors). In addition, the theory is very complex.
Construction of a copper coil heat exchanger
-
- Moderator
- posts: 79390
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11076
-
- Moderator
- posts: 79390
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11076
It's been an hour that I take my head with precise calculations that lead to nothing for the simple problem that we face.
For those who want to have fun: http://www.librecours.org/documents/8/899.pdf
Here is a very simplified approach:
http://fr.wikipedia.org/wiki/Transfert_ ... _thermique
By browsing the net a bit I found that a copper exchanger had a real K varying from 400 to 800 W / m². ° C (if there are specialists in the room ... average values depending on the form of the exchanger would be interesting)!
Consider 400, the worst case, with a T ° delta of 10 ° C, the tigger exchanger would therefore have a power of:
P = 400 * 10 * 1,73 = 6,9 kW
So Owen, you would need an exchanger of more than 1.5m² of exchange surface.
With 22mm Copper this gives a length of at least: 21,4 m far from the 6m that you "thought" ...
But we are stupid: so look at the surface of the tubes of your solar panels ... by taking the same you will not be far from what you need in your buffer ...
Tigger how did you size your streamer?
For those who want to have fun: http://www.librecours.org/documents/8/899.pdf
Here is a very simplified approach:
http://fr.wikipedia.org/wiki/Transfert_ ... _thermique
By browsing the net a bit I found that a copper exchanger had a real K varying from 400 to 800 W / m². ° C (if there are specialists in the room ... average values depending on the form of the exchanger would be interesting)!
Consider 400, the worst case, with a T ° delta of 10 ° C, the tigger exchanger would therefore have a power of:
P = 400 * 10 * 1,73 = 6,9 kW
So Owen, you would need an exchanger of more than 1.5m² of exchange surface.
With 22mm Copper this gives a length of at least: 21,4 m far from the 6m that you "thought" ...
But we are stupid: so look at the surface of the tubes of your solar panels ... by taking the same you will not be far from what you need in your buffer ...
Tigger how did you size your streamer?
0 x
Do a image search or an text search - Netiquette of forum
Hello
Tigger's coil looks efficient
Otherwise you can download this spreadsheet available on Apper
http://forum.apper-solaire.org/download.php?id=12
Attention, the delta T is the difference between the heat transfer fluid which circulates in the coil and the liquid contained in the balloon
For my 1500L buffer I will start on 50 m of copper D22 ep 1
A+
Tigger's coil looks efficient
Otherwise you can download this spreadsheet available on Apper
http://forum.apper-solaire.org/download.php?id=12
Attention, the delta T is the difference between the heat transfer fluid which circulates in the coil and the liquid contained in the balloon
For my 1500L buffer I will start on 50 m of copper D22 ep 1
A+
0 x
-
- Moderator
- posts: 79390
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11076
I haven't built, but we have this in our buffer, the surface of which must be several dozen m²!
Cf: https://www.econologie.com/forums/tampon-the ... t4517.html
Cf: https://www.econologie.com/forums/tampon-the ... t4517.html
0 x
Do a image search or an text search - Netiquette of forum
Calculation of the exchanger coil as a function of the collector area
http://forum.apper-solaire.org/download.php?id=14
A+
http://forum.apper-solaire.org/download.php?id=14
A+
0 x
-
- Moderator
- posts: 79390
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11076
Information
Sorry, but you are not authorized to view or download this file
Same looping!
Don't you want to put them on the ecp host ecp?
0 x
Do a image search or an text search - Netiquette of forum
-
- Moderator
- posts: 79390
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11076
Yes it looks like but in fact they are batteries from (large) air conditioning units. They are 3 m long, 30 cm wide and about 1 m high.
The new unit price must tate the 5000 € (I suppose they are therefore of recovery?).
The new unit price must tate the 5000 € (I suppose they are therefore of recovery?).
Last edited by Christophe the 10 / 09 / 08, 10: 00, 1 edited once.
0 x
Do a image search or an text search - Netiquette of forum
-
- Similar topics
- Replies
- views
- Last message
-
- 28 Replies
- 8306 views
-
Last message by Philippe Schutt
View the latest post
08/12/22, 09:28A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 29 Replies
- 19486 views
-
Last message by Ahmed
View the latest post
08/10/12, 14:06A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 18 Replies
- 9585 views
-
Last message by Philippe Schutt
View the latest post
17/06/12, 10:13A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 3 Replies
- 9957 views
-
Last message by Ahmed
View the latest post
06/01/12, 12:55A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 12 Replies
- 6809 views
-
Last message by dedeleco
View the latest post
16/11/11, 01:28A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : role and 375 guests