Pellematic Condes 25 kW: setting?

Heating, insulation, ventilation, VMC, cooling ... short thermal comfort. Insulation, wood energy, heat pumps but also electricity, gas or oil, VMC ... Help in choosing and implementation, problem solving, optimization, tips and tricks ...
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 13/02/23, 10:59

In principle, when the circulator is stopped it should on the contrary be completely closed if I refer to my own v3v.

Especially since your valve was ordered only at closing since 5:39 this day!

So, I would advise you to close it completely to see how it revives once your ambient temperature has dropped.
1 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 13/02/23, 11:08

Pilpoill wrote:In principle, when the circulator is stopped it should on the contrary be completely closed if I refer to my own v3v.

Especially since your valve was ordered only at closing since 5:39 this day!

So, I would advise you to close it completely to see how it revives once your ambient temperature has dropped.


It is done
Attachments
20230213_110728.jpg
1 x
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 25/02/23, 08:42

Hello,

I think Tulul63 is busy so I allow myself a little message here.

The problem was due to the v3v which was badly positioned and which allowed too much hot water to pass (not to mention the inverted open/closed markers).
However, it seemed closed according to the position of its indicator, so nothing replaces the presence in front of its boiler according to the malfunctions encountered.
It is Tulul63 who found by deduction 8)
1 x
User avatar
Obamot
Econologue expert
Econologue expert
posts: 28725
Registration: 22/08/09, 22:38
Location: regio genevesis
x 5538

Re: Pellematic Condes 25 kW: adjustment?




by Obamot » 25/02/23, 19:49

Thanks for your comments too!

tulul63 wrote:
Pilpoill wrote:In principle, when the circulator is stopped it should on the contrary be completely closed if I refer to my own v3v.

Especially since your valve was ordered only at closing since 5:39 this day!

So, I would advise you to close it completely to see how it revives once your ambient temperature has dropped.


It is done

Welcome to this fo-fo and thank you for the feedback!
1 x

 