Pellematic Condes 25 kW: setting?

Heating, insulation, ventilation, VMC, cooling ... short thermal comfort. Insulation, wood energy, heat pumps but also electricity, gas or oil, VMC ... Help in choosing and implementation, problem solving, optimization, tips and tricks ...
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 01:33

Pilpoill wrote:Good evening, the water law is too strong, it still triggers despite the cut-off hysteresis at 1K and there are probably many other things to study.

A photo of the circulator (in operation if it is led) to see how it is configured.
Is the flow temperature sensor firmly attached to the flow pipe? (Normally positioned above the circulator)
How many radiators and their type for this surface?
Are they all open to the maximum if they are fitted with a thermostatic valve?


Yes the temperature sensor is firmly attached to the flow pipe
14 aluminum radiators with cast iron core (high temperature: it was an old installation with gas condensing boiler)
all the radiators are fitted with a thermostatic valve and they are not all fully open
here is the photo of the circulator
Attachments
20230212_012108 [1] .jpg
0 x
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 12/02/23, 22:25

Too bad for me, it does not look like the usual hydraulic block from Okofen.

First point, your v3v pumps for hours before stabilization.
Would you have the precise references of the circulator and this v3v stp?
0 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 22:38

Pilpoill wrote:Too bad for me, it does not look like the usual hydraulic block from Okofen.

First point, your v3v pumps for hours before stabilization.
Would you have the precise references of the circulator and this v3v stp?


Here is a photo of each element with the references
Attachments
20230212_223312.jpg
20230212_223317.jpg
0 x
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 12/02/23, 23:21

If your installation is in twin-tubes, the instructions in paragraph 7.5 https://api.grundfos.com/literature/Gru ... 014888.pdf indicates to set to proportional pressure mode. Is this the case? (I only see speed III)
0 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 23:37

Pilpoill wrote:If your installation is in twin-tubes, the instructions in paragraph 7.5 https://api.grundfos.com/literature/Gru ... 014888.pdf indicates to set to proportional pressure mode. Is this the case? (I only see speed III)

Yes my installation is indeed in twin pipe
And indeed on the record it is precaunise to be proportional.
In operation the indicated value varies well
0 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 23:43

Pilpoill wrote:If your installation is in twin-tubes, the instructions in paragraph 7.5 https://api.grundfos.com/literature/Gru ... 014888.pdf indicates to set to proportional pressure mode. Is this the case? (I only see speed III)
Pilpoill wrote:If your installation is in twin-tubes, the instructions in paragraph 7.5 https://api.grundfos.com/literature/Gru ... 014888.pdf indicates to set to proportional pressure mode. Is this the case? (I only see speed III)

Do you want me to modify by pressing the circulator
0 x
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 12/02/23, 23:45

For me, you are in a constant curve, this is the position for the ECS according to the instructions (line 5)

You must be in line 0 (speed II) or line 2 (speed III)

A49FC53E-CE5A-423F-AF99-BC55E1324B83.jpeg
A49FC53E-CE5A-423F-AF99-BC55E1324B83.jpeg (275.9 KiB) Viewed 1644 times
0 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 23:51

Pilpoill wrote:For me, you are in a constant curve, this is the position for the ECS according to the instructions (line 5)

You must be in line 0 (speed II) or line 2 (speed III)

A49FC53E-CE5A-423F-AF99-BC55E1324B83.jpeg

I put it in gear II
Attachments
20230212_234858.jpg
0 x
Pilpoill
I understand econologic
I understand econologic
posts: 164
Registration: 12/11/17, 09:55
x 37

Re: Pellematic Condes 25 kW: adjustment?




by Pilpoill » 12/02/23, 23:51

I like it 8)

To be continued tomorrow : Wink:
0 x
tulul63
I learn econologic
I learn econologic
posts: 18
Registration: 10/02/23, 13:42
x 5

Re: Pellematic Condes 25 kW: adjustment?




by tulul63 » 12/02/23, 23:53

Pilpoill wrote:I like it 8)

To be continued tomorrow : Wink:


thank you and good evening
0 x

 