Hello everyone
Since 2 days, when I go home or before yesterday during the night, I have my main breaker that trips.
At my switchboard, none of the circuit breakers has tripped.
But my table is to redo. It's DIY.
How can I test a circuit or something else to determine which circuit is involved?
Thank you
freaks counter
Re: Trip counter
There are two possibilities to blow the main circuit breaker:moby25 wrote:Since 2 days, when I go home or before yesterday during the night, I have my main breaker that trips.
1) Exceeding the authorized power (if you have an 45A subscription, you put 5 circuits to 10A: none of the circuits are in default but the total exceeds). If you have an EDF electronic meter, it must memorize the maximum value that has passed.
2) The "differential circuit breaker" function trips. If your switchboard is not equipped with one or more RCDs (generally 30 mA), a current leak to earth is only detected by the RCD of the main circuit breaker. As this is a random problem, it is not easy to find the cause ...
You can (current cut) measure the resistance of each circuit with respect to the ground, but if it is a equipment which causes the escape, it can only take place when it is lit ...
0 x
Indeed, it can be a boring erratic thing!
All the same, when you find the disjointed general, you lower the breakers of all your lines.
You surrender the general.
And you go up each line one by one. Hopefully this will jump out the moment you snap the faulty "branch".
With a bit of luck...
And if it works, you do the same by unplugging all the devices involved and you reconnect one by one, until it jumps. And you have the culprit.
But actually, if it's just the limit of tolerated leaks, it may not jump when you try and jump later.
I forgot: a priori, only suspect devices with an earth connection (therefore a plug with the metallic "titonniot" in the middle). The others (simple plug with two connectors) are not earthed and do not cause leakage current ...
All the same, when you find the disjointed general, you lower the breakers of all your lines.
You surrender the general.
And you go up each line one by one. Hopefully this will jump out the moment you snap the faulty "branch".
With a bit of luck...
And if it works, you do the same by unplugging all the devices involved and you reconnect one by one, until it jumps. And you have the culprit.
But actually, if it's just the limit of tolerated leaks, it may not jump when you try and jump later.
I forgot: a priori, only suspect devices with an earth connection (therefore a plug with the metallic "titonniot" in the middle). The others (simple plug with two connectors) are not earthed and do not cause leakage current ...
0 x
Two categories of devices are suspected a priori: those subject to corrosion (washing machine, etc ...) and those exposed to moisture (I had a problem of the kind with an old electric hot plate , with the buttons that turn: overflow of boiling water, sank under the button, seal not tight, leakage current, tripping well after - it took time for it to penetrate; to say that it can be "boring"!)
0 x
-
- Grand Econologue
- posts: 865
- Registration: 10/05/09, 16:39
- x 21
I forgot: a priori, only suspect devices with an earth connection (therefore a plug with the metallic "titonniot" in the middle). The others (simple plug with two connectors) are not earthed and do not cause leakage current ...
The current leak on the ground can come from the female side of the socket (the wall socket).
The case has already happened to me twice. Yet with quality sockets (Legrand).
0 x
Save a tree, eat a beaver.
It is no use to succeed in life, what it takes is to miss his death.
It is no use to succeed in life, what it takes is to miss his death.
-
- Grand Econologue
- posts: 865
- Registration: 10/05/09, 16:39
- x 21
- chatelot16
- Econologue expert
- posts: 6960
- Registration: 11/11/07, 17:33
- Location: Angouleme
- x 264
if you want to move forward, answer the questions!
do you have an electronic counter? if yes it keeps in memory the maximum power consumed, you will see if it is the power that blew up ... otherwise it is necessary to think a little more
what kind of disjonteur? on which current is it regulated? 15A? 30A ...?
is it differential? what differential current? 500mA?
list of connected appliances ... electric heater, machine
first advice: debranche completely everything you do not use ... if it jumps when you reconnect you will have the culprit!
do you have an electronic counter? if yes it keeps in memory the maximum power consumed, you will see if it is the power that blew up ... otherwise it is necessary to think a little more
what kind of disjonteur? on which current is it regulated? 15A? 30A ...?
is it differential? what differential current? 500mA?
list of connected appliances ... electric heater, machine
first advice: debranche completely everything you do not use ... if it jumps when you reconnect you will have the culprit!
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 13 Replies
- 20941 views
-
Last message by chatelot16
View the latest post
12/09/17, 21:54A subject posted in the forum : Electricity, electronics and IT Hi-Tech, Internet, DIY, lighting, materials and new
-
- 20 Replies
- 17345 views
-
Last message by izentrop
View the latest post
04/01/17, 11:16A subject posted in the forum : Electricity, electronics and IT Hi-Tech, Internet, DIY, lighting, materials and new
-
- 0 Replies
- 8744 views
-
Last message by Christophe
View the latest post
05/02/15, 11:48A subject posted in the forum : Electricity, electronics and IT Hi-Tech, Internet, DIY, lighting, materials and new
-
- 35 Replies
- 21473 views
-
Last message by Did67
View the latest post
23/08/13, 14:42A subject posted in the forum : Electricity, electronics and IT Hi-Tech, Internet, DIY, lighting, materials and new
-
- 40 Replies
- 25553 views
-
Last message by I Citro
View the latest post
15/11/10, 22:53A subject posted in the forum : Electricity, electronics and IT Hi-Tech, Internet, DIY, lighting, materials and new
Who is online ?
Users browsing this forum : No registered users and 245 guests