COP actual measurement air conditioning Airton Inverter




by Christophe » 12/07/13, 13:23

I just estimate the actual thermal performance of an air conditioning Airton. In calculating the actual COP.

The external battery of this heat pump is installed
in a greenhouse: https://www.econologie.com/forums/clim-rever ... 12393.html

Image

The results are quite impressive for a measure (the stabilized exceeds 5 COP), for the rest it fits with the manufacturer data !! So all good!

datasheet:

Image

Measurement conditions

Outdoor T ° (in the greenhouse): 36 ° C / 48% RH

° Indoor: 25.2 ° C

temperature set aircon: 32 ° C (max to avoid regulations)

blowing area of ​​the air conditioning: 0.0536 m²

Prince measures

Principle: it is estimated the power of the air blown by the air conditioning by measuring flow and temperatures.

Measurements made with this anemometer which gives the velocity and T ° instantaneous airflow.

Image

Protocol: I 4 measurement points along the fan, as perpendicular as possible to the flow, I note and T ° km / h at each point.

T ° should therefore stabilize I measure 1 minute after moving the anemometer.

We take the averages of these 4 points and we obtain a measurement of volume flow and "hot" T °.

I corrects the flow rate with the density of air (which varies greatly between 25 and 40 ° C) to obtain the mass air flow.

With indoor T °, ​​it is a heat balance and we get the power restored heater.

I measure the electrical power consumed by a power meter on outlet

COP is obtained by dividing the 2!

Measures (performed at 10 minute intervals beginning at T = 10 min and in chronological order)

1 measure:

Pu = 1032W

Image

T ° = inner 25.2 ° C
T ° = Hot 33.38 ° C
4.72 blower speed = m / s
Volume flow = 0.2527 m3 / s
Density at 32.5 1.155 ° C = kg / m3
( according to http://fr.wikipedia.org/wiki/Masse_volumique_de_l%27air )
Mass flow = 0.2919 kg / s
Pc 1004 air = J / kg. ° C

Power output W = 2396

COP = 2.32


2 measure:

Pu = 950W

Image

Image

T ° = inner 25.2 ° C
T ° = Hot 36 ° C
4.35 blower speed = m / s
Volume flow = 0.2330 m3 / s
Density at 35 1.146 ° C = kg / m3

Mass flow = 0.2670 kg / s
Pc 1004 air = J / kg. ° C

Power output W = 2889

COP = 3.04




3 measure:

Pu = 650W

Image

T ° = inner 25.2 ° C
T ° = Hot 39.4 ° C
4.19 blower speed = m / s
Volume flow = 0.2245 m3 / s
Density at 40 1.127 ° C = kg / m3
Mass flow = 0.2530 kg / s
Pc 1004 air = J / kg. ° C

Power output W = 3593

COP = 5.53
: Shock: : Shock:

In short it is good: the best COP is obtained in the most steady (after 30 minutes of operation). I would do one measure after 1 hours of operation and in slightly different conditions.

I think that the presence of the external battery in a greenhouse at 36 ° C is not unrelated to this "boost" of the COP !!
Last edited by Christophe the 19 / 07 / 13, 10: 16, 1 edited once.
0 x
User avatar
chatelot16
Econologue expert
Econologue expert
posts: 6960
Registration: 11/11/07, 17:33
Location: Angouleme
x 264




by chatelot16 » 12/07/13, 13:50

a cop 5 it sounds good ... but with a superior outdoor temperature at the indoor temperature, the cop should be infinite!

the heat should go alone without the need to pump!
Last edited by chatelot16 the 12 / 07 / 13, 14: 21, 1 edited once.
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 12/07/13, 14:09

It is not wrong Chatelot! Myself have done or what? : Cheesy:

The problem is that the wall between the greenhouse and the room or the CAP is now ... well insulated! : Cheesy:
0 x
User avatar
hic
Grand Econologue
Grand Econologue
posts: 995
Registration: 04/04/08, 19:50
x 5

Re: COP actual measurement air conditioning Airton Inverter




by hic » 12/07/13, 14:57

Christophe wrote:The results are quite impressive for a measure (the stabilized exceeds 5 COP), for the rest it fits with the manufacturer data !! So all good!

(...)

I think that the presence of the external battery in a greenhouse at 36 ° C is not unrelated to this "boost" of the COP !!


Hello

you do not know
the 'cop constructreur is normalized to 7 °?
(Part of course)


Standard: EN 14511-2
*** http://www.energy.ca.gov/title24/2008st ... 007%29.pdf ***

compressed air at 36 °,
your machine is not made to ca
0 x
"Let food be thy medicine and thy medicine be thy food" Hippocrates
"Everything has a price has no value" Nietzche
Torture for Dummies
Forbid to express the idea that the field is acceleration (magnetic and gravitational)
And you get your patent mental torture option executioner successfully
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 12/07/13, 15:59

And then Hic? What's the difference?

What matters are the actual performance observed no? To confirm whether the installation of the outdoor unit in a greenhouse!

Chatelot's remark was more relevant than yours!

And I surely no thermal lessons from a guy who mix kW and kWh ... (I say this because in his previous post I deleted Hic called me ignorant of red and more. ..)

In fact the red is for moderation, you're not speaking I think? if?

It is not air which is compressed to 36 ° C but the fridge gas ...

Anyway ... this confirms it ...
0 x
User avatar
chatelot16
Econologue expert
Econologue expert
posts: 6960
Registration: 11/11/07, 17:33
Location: Angouleme
x 264




by chatelot16 » 12/07/13, 16:14

if the heat pump was reverssible thermodynamically it should in this case generate electricity!

the pressure in the evaporator in the greenhouse is superior to the pressure in the condenser in the house ... so it is no longer a need but a compressor motor freon vapor, which produces mechanical energy

although the rest of the Pac Nor should: to return the liquid inside to the outside, the pressure regulator or the capillary does not work! would require a pump! as the fuel pump of a steam engine!
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 12/07/13, 16:18

Chatelot thin, got screwed lol!

Yes, it still consumes (but consumption has fallen precipitously!)

I would have to redo a consumption monitoring test only!

In any case it works as manual says that above 25 ° C outdoor heat pump function (heating) should not walk ...
0 x
Alain G
Econologue expert
Econologue expert
posts: 3044
Registration: 03/10/08, 04:24
x 3

Re: COP actual measurement air conditioning Airton Inverter




by Alain G » 12/07/13, 16:49

Hic wrote:
Christophe wrote:The results are quite impressive for a measure (the stabilized exceeds 5 COP), for the rest it fits with the manufacturer data !! So all good!

(...)

I think that the presence of the external battery in a greenhouse at 36 ° C is not unrelated to this "boost" of the COP !!


Hello

you do not know
the 'cop constructreur is normalized to 7 °?
(Part of course)


Standard: EN 14511-2
*** http://www.energy.ca.gov/title24/2008st ... 007%29.pdf ***

compressed air at 36 °,
your machine is not made to ca



This is not really a problem if ventilation of the condenser is large enough, more if the air conditioner has a high-pressure safety arrêtra it simply to avoid the compressor pump the liquid.
0 x
Stepping behind sometimes can strengthen friendship.
Criticism is good if added to some compliments.
Alain
Alain G
Econologue expert
Econologue expert
posts: 3044
Registration: 03/10/08, 04:24
x 3




by Alain G » 12/07/13, 16:53

Christophe wrote:Chatelot thin, got screwed lol!

Yes, it still consumes (but consumption has fallen precipitously!)

I would have to redo a consumption monitoring test only!

In any case it works as manual says that above 25 ° C outdoor heat pump function (heating) should not walk ...


So it has a high-pressure safety!


As I said above if ventilation of the condenser is large enough it is not a problem but if you sure that decreases the ventilation has probably 2 or three speeds it will stop.
0 x
Stepping behind sometimes can strengthen friendship.

Criticism is good if added to some compliments.

Alain
raymon
Grand Econologue
Grand Econologue
posts: 901
Registration: 03/12/07, 19:21
Location: vaucluse
x 9




by raymon » 12/07/13, 17:05

In the case of an AC inverter compressor with 2 story like mine the cop is not it much better at low power because the surface of the pipes in the outer group is much larger compared to the energy consumed?

That did the top cop when 300w consumes rather than 800w?