Hi there. I ordered the EVT720 micro inverter from Invertech.
I have 6 solar panels of 150W each in 12V, i.e. 22V in open circuit and 8A each, currently connected in parallel to a small 12V inverter. Total theoretical power therefore 900W.
The new Invertech micro-inverter has an operating range of between 16V and 60V, but if I leave my panels there in parallel, the 22V voltage they will send to it will probably be too tight to make it work properly. performance, especially since they would send him more than 40A when he can only collect 12 on each input. So I plan to connect them in series. Except that the micro inverter only has two panel inputs.
My problem is that: if I make two series of three panels, they will each send 66V to the inverter (3x22 volts) on 8A, knowing that it only supports 60V maximum. I therefore plan to connect two series of two panels to it (44 volts each at 8A) and the last series of the last two panels connected in parallel to one of the other two. But that seems a bit barbaric to me. According to you? Especially since it would be 44V but at 16A.
In the end, I think I can only settle for two sets of 2 panels. 2X22 volts in series on 8A per inverter input. But first, I still prefer to ask your opinion, my knowledge being limited. The last two panels will serve me for something else independent.
Here are some photos. First the inverter.
The technical aspect:
And finally, the assembly that I envisage.
Serial or parallel micro inverter connection
-
- Econologue expert
- posts: 9803
- Registration: 31/10/16, 18:51
- Location: Lower Normandy
- x 2658
Re: Serial or parallel micro inverter connection
Hello Darween,
I will not venture into this field because I have no personal experience, but I note that in your proposal the second circuit could deliver up to 16A while the "maximum input" of each input is 12A according to the technical sheet.
Are you sure that your panels deliver "in real life" 22V? With a little less, a solution with 2 times three panels in series would perhaps be possible? This is only a lead, certainly not a recommendation, others than me may be able to tell you.
I will not venture into this field because I have no personal experience, but I note that in your proposal the second circuit could deliver up to 16A while the "maximum input" of each input is 12A according to the technical sheet.
Are you sure that your panels deliver "in real life" 22V? With a little less, a solution with 2 times three panels in series would perhaps be possible? This is only a lead, certainly not a recommendation, others than me may be able to tell you.
0 x
-
- Econologue expert
- posts: 13698
- Registration: 17/03/14, 23:42
- Location: picardie
- x 1516
- Contact :
Re: Serial or parallel micro inverter connection
Hello,
I also think that the maximum values will depend on the place where you are and the orientation.
If we choose to orient them for maximum efficiency in mid-season, they will not deliver their maximum power, nor their maximum open-load voltage at the height of summer.
Moreover, by adding bypass diodes, the MPPT power point changes https://energieplus-lesite.be/theories/ ... oltaiques/
Are you sure about 22v? did you measure it? https://allo.solar/panneau-solaire-150w ... iteck.html
I also think that the maximum values will depend on the place where you are and the orientation.
If we choose to orient them for maximum efficiency in mid-season, they will not deliver their maximum power, nor their maximum open-load voltage at the height of summer.
Moreover, by adding bypass diodes, the MPPT power point changes https://energieplus-lesite.be/theories/ ... oltaiques/
Are you sure about 22v? did you measure it? https://allo.solar/panneau-solaire-150w ... iteck.html
0 x
Re: Serial or parallel micro inverter connection
*izentrop wrote:Hello,
I also think that the maximum values will depend on the place where you are and the orientation.
If we choose to orient them for maximum efficiency in mid-season, they will not deliver their maximum power, nor their maximum open-load voltage at the height of summer.
Moreover, by adding bypass diodes, the MPPT power point changes https://energieplus-lesite.be/theories/ ... oltaiques/
Are you sure about 22v? did you measure it? https://allo.solar/panneau-solaire-150w ... iteck.html
Yes, I have already measured no load, it is between 21 and 22 V, and often even 22V. The panels are already equipped with diodes to avoid swinging their potatoes between them. So, it would be better to avoid being too fair for the inverter, because my panels are due south with a tilt angle of 39/40° so they are, in a way, optimized at best.
I therefore think to start with 2 series of 2 panels in series, to make 44 volts in 8A, it will be ok for each input of the inverter with enough safety margin not to burn or to heat the inverter at the limit of its capacities. And I can then buy another micro inverter for the last 2 panels. That's all I can see.
My panels are Enjoy Solar brand monocrystalline, ECO LINE ES150M36 models, their open circuit voltage is given as 22,8V for 8,12A
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 11 Replies
- 1578 views
-
Last message by preliator
View the latest post
18/01/24, 16:18A subject posted in the forum : Renewable energy: solar power
-
- 20 Replies
- 2602 views
-
Last message by plasmanu
View the latest post
09/11/23, 14:21A subject posted in the forum : Renewable energy: solar power
-
- 41 Replies
- 37684 views
-
Last message by Remundo
View the latest post
24/11/21, 20:35A subject posted in the forum : Renewable energy: solar power
-
- 8 Replies
- 6459 views
-
Last message by izentrop
View the latest post
19/02/20, 10:14A subject posted in the forum : Renewable energy: solar power
-
- 9 Replies
- 15128 views
-
Last message by plasmanu
View the latest post
10/01/20, 03:34A subject posted in the forum : Renewable energy: solar power
Back to "Renewable energy: solar electricity"
Who is online ?
Users browsing this forum : No registered users and 228 guests