Boiler control okofen




by casuette » 08/10/17, 11:44

Hello,
The weather Being gray this day and the outside temperature at 14 ° I take the opportunity to make my adjustments. Here they are:
Scheduled comfort home temp: 19,5 °, reduced house temp: 17 °
I have time slots: week: 7 to 11 a.m. then 17 to 21 p.m.,
Curve: 30 and foot 1,1
What I don't understand is the temperature at which the water starts. Today it's 14 ° outside so if I apply the formula:
1,1 X (19,5-14) + 30 = 38,5 °. The boiler shows me CF1 start temp 29,5 °. If I understood correctly from the formula, it should be 38,5 °? The temperature in the house is 19 °.
My question therefore concerns the starting water temperature displayed by the boiler in CF1 which should be higher, right?
What to do? Thank you for your advice.
0 x
Gobitcho
I learn econologic
I learn econologic
posts: 12
Registration: 11/03/19, 20:49

Re: Okofen boiler adjustment




by Gobitcho » 01/10/22, 08:35

Hello, you are wrong in your calculations.

1,1x(19,5-14)+30 = 36,05

cordially
0 x
phil59
Econologue expert
Econologue expert
posts: 2212
Registration: 09/02/20, 10:42
x 504

Re: Okofen boiler adjustment




by phil59 » 03/10/22, 00:16

Effectively ! : Lol: : Arrow: : Arrow: : Arrow: : Arrow: : Arrow: : Arrow:
0 x
hmmmmm, hmmmmmmmmmmmmm, hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhmmmmmmmmm, huh, hmmmmmmmmmmmmm.

: Oops: : Cry: :( : Shock:

 


  • Similar topics
    Replies
    views
    Last message

Back to "Heating, insulation, ventilation, VMC, cooling ..."

Who is online ?

Users browsing this forum : No registered users and 294 guests