max 01 wrote:
If you can collect information for a mechanical limitation of the power it would be perfect because I saw on this site that it would take a burner operating time between 30 and 40 'and a downtime of about 20 ', to obtain optimum performance and limit wear and tear on the boiler by a succession of steps / stops.
cordially
1) A 25 cannot, in fact, be physically reduced to less than 22 kW. How you can't make a city car out of a van!
To go below, it's another "carcass", the 20-15-12-10 [depending on the number of open exchangers, and the programming, the same "carcass" can cover all these needs.
2) The downtime of 20 ', I don't see ??? Don't seem serious to me.
On the other hand, in fact, the average burner time, in fact, is an important indicator of proper operation.
There is no amxi.
But low average, below 1/2, are the sign of a "yoyo" operation, incessant walking / stopping.
Generally linked to overkill.
But can also be linked to bad settings.
Besides the P114, two things to note to "pose" the diagnosis:
- what is the boiler temperature reached when it initiates the shutdown procedure?
- what is the modulation level (P162) reached just when stopping ...