Re: Photovoltaic connection of PV???




by phil59 » 01/03/23, 20:09

Forhorse wrote:
phil59 wrote:
Between 5 and 100m, the section will not support the same at all.



The section supports the same whatever the length of the cable...
It's just that the losses by Joule effect end up making that over too great a distance there is nothing left at the end.


Yes!
0 x
hmmmmm, hmmmmmmmmmmmmm, hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhmmmmmmmmm, huh, hmmmmmmmmmmmmm.

: Oops: : Cry: :( : Shock:
chris34
I understand econologic
I understand econologic
posts: 110
Registration: 18/08/11, 17:34
Location: Lodeve (34)
x 4
Contact :

Re: Photovoltaic connection of PV???




by chris34 » 02/03/23, 18:46

Thanks for all your quick responses! :-)

Details my PV date from 2011 (it makes them 12 years). It's true that I could have kept them a little longer but I've just had a small return of pesetas :D .... It's also true that returns have nothing to do with it. :P

I will dig on the technical docs to see the characteristics of the chargers / regulators ....
My distances do not exceed 5 meters ...

C.
0 x
Chris34
Christophe
Moderator
Moderator
posts: 79114
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10972

Re: Photovoltaic connection of PV???




by Christophe » 02/03/23, 19:13

If you have extra pesetas and spare space, then keep the old string and add an inverter (if necessary)
0 x
phil59
Econologue expert
Econologue expert
posts: 2212
Registration: 09/02/20, 10:42
x 504

Re: Photovoltaic connection of PV???




by phil59 » 02/03/23, 19:15

chris34 wrote:Thanks for all your quick responses! :-)

Details my PV date from 2011 (it makes them 12 years). It's true that I could have kept them a little longer but I've just had a small return of pesetas :D .... It's also true that returns have nothing to do with it. :P

I will dig on the technical docs to see the characteristics of the chargers / regulators ....
My distances do not exceed 5 meters ...

C.


If I were in your case, and as I have the space, I would add more, but would not replace.
0 x
hmmmmm, hmmmmmmmmmmmmm, hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhmmmmmmmmm, huh, hmmmmmmmmmmmmm.

: Oops: : Cry: :( : Shock:
chris34
I understand econologic
I understand econologic
posts: 110
Registration: 18/08/11, 17:34
Location: Lodeve (34)
x 4
Contact :

Re: Photovoltaic connection of PV???




by chris34 » 02/03/23, 19:23

.... my current concern is to choose CHARGERS (Regulators) therefore between the PV and my battery pools. I have 2 PWMs and an MPPT currently, but I'm thinking of ending only MPPTs... :)
0 x
Chris34
chris34
I understand econologic
I understand econologic
posts: 110
Registration: 18/08/11, 17:34
Location: Lodeve (34)
x 4
Contact :

Re: Photovoltaic connection of PV???




by chris34 » 02/03/23, 19:26

...well, no, precisely I don't have much space!! : Cry:
0 x
Chris34
sicetaitsimple
Econologue expert
Econologue expert
posts: 9772
Registration: 31/10/16, 18:51
Location: Lower Normandy
x 2638

Re: Photovoltaic connection of PV???




by sicetaitsimple » 02/03/23, 19:28

chris34 wrote:Details my PV date from 2011 (it makes them 12 years). It's true that I could have kept them a little longer but I've just had a small return of pesetas :D .... It's also true that returns have nothing to do with it. :P

Beyond your personal case, and of course you do what you want, it still brings me some questions.
"The PV industry", in the broad sense, does not stop communicating on performances that are little affected over time (I have in mind an order of magnitude of more than 80% of the guaranteed peak power after 20 years) and a lifetime well above this value of 20 years.
It would be rubbish, we will necessarily replace these panels at the deadline or before? In which case we would have made unequipped electricity consumers pay substantial and fixed purchase prices for 20 years without benefiting for let's say 10 more years from a minimum cost price, the capital being amortized?
In short, a PV installation under feed-in tariff would only last the period of the feed-in tariff?

PS: once again, I'm not targeting Chris34 who also seems to be on an isolated site, so nothing to do.
1 x
Christophe
Moderator
Moderator
posts: 79114
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10972

Re: Photovoltaic connection of PV???




by Christophe » 02/03/23, 19:32

Ah indeed if on battery it changes the situation...

That's why I asked for an update diagram...
1 x
chris34
I understand econologic
I understand econologic
posts: 110
Registration: 18/08/11, 17:34
Location: Lodeve (34)
x 4
Contact :

Re: Photovoltaic connection of PV???




by chris34 » 02/03/23, 19:53

Correct: I forgot to specify. : Oops: : I am in an ISOLATED SITE!!!! :?
So my PV feed my batteries via ... my future REGULATORS ;-)

So, yes OK: I'm doing a little diagram...tomorrow I promise!
Good evening to all !
1 x
Chris34
chris34
I understand econologic
I understand econologic
posts: 110
Registration: 18/08/11, 17:34
Location: Lodeve (34)
x 4
Contact :

Re: Photovoltaic connection of PV???




by chris34 » 05/03/23, 18:38

IMG_20230305_181225 [1] .jpg
my setup today


IMG_20230305_181248 [1] .jpg
my install...soon


well, here is what I thought to load my 3 Strings:

1) an MPPT 100 / 50 A which will receive 1640 W (1440 W max recommended) => for the PARC2 of batteries
2) an MPPT 100 / 30 A which will receive 820 W (max. 880 W recommended) => for the PARC1 of batteries
3) a 100 / 30 A MPPT which will receive 820 W (max. 880 W recommended) => for the PARC1 of batteries

Knowing that the PV Modules are 410 W / ISC = 13,77 A and VOC = 37,45 V

The archi of the 3 PV Fields (positioned on different supports):
1) 4 Modules in series-parallel => 75 V / 28 A
2) 2 Modules in series => 75 V / 13,77 A
3) 2 Modules in series => 75 V / 13,77 A

Hence my question: do you see a wolf in these estimates...? : Shock: : Shock:
1 x
Chris34

 