Philippe Schutt wrote:"Volcano" burners have 3 operating states:
1- off
2- combustion
3- standby
If the first 2 states pose no problem, the 3rd is debatable.
Indeed, in this state, the boiler cuts the arrival of pellets and the mechanical supply of air, so as to maintain a block of embers in the burner. The combustion is then horrible, polluting and clogs the duct, in particular the anti-bird grilles. This block of embers can last a good half hour, depending on the natural draft of the chimney.
The advantage (and justification) of this system is a very rapid restart of the boiler, allowing the buffer tank to be dispensed with. Hence a saving of almost €1000 on the installation, or a more stable regulation of the T° in the house.
It is very important not to oversize the boiler, to limit these phases. However, installers do this systematically, especially those who are used to oil or gas heaters.
To limit breakage, I suggest programming periods of complete shutdown and limiting the maximum power.
What you call the "eve" is not exactly what you describe at Okofen
Once the end of combustion has been ordered, there is a post-ventilation time for the fireplace that can go on a Compact up to 600 or even 1800 seconds (depending on power 10/18kW or 22/32kW) to allow the end of combustion of the pellets present on the combustion plate.
The real time is calculated according to a temperature delta set by Okofen.