Duval thema c23E saunier sanitary failure




by danpel » 21/07/20, 10:08

Hello,

my boiler no longer produces hot water although the heating side is working fine.
I replaced the water valve and the reversing valve but nothing helps, when the water is drawn the boiler does not trigger, if I manually use the microswitch it works.
Do you have an idea ?

Thank you

Daniel
0 x
Christophe
Moderator
Moderator
posts: 79118
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10973

Re: Malne sanitary saunier duval thema c23E




by Christophe » 21/07/20, 14:29

From what you explain the boiler does not detect the flow of sanitary water .... so it's definitely a problem with the flowmeter.

I don't know how exactly the DHW flow rate is detected on gas boilers, but there is necessarily a sensor.

Maybe a differential pressure sensor?
0 x
Christophe
Moderator
Moderator
posts: 79118
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10973

Re: Malne sanitary saunier duval thema c23E




by Christophe » 21/07/20, 14:31

Here is a Saunier Duval flow sensor: https://www.piecesxpress.com/article-11 ... -duval.htm

107013.jpg
107013.jpg (17.77 KB) Viewed times 10451


Is that what you call water valve? If yes look at the multimeter if it works and if so look where it is connected (a relay maybe?)
0 x
danpel
I discovered econologic
I discovered econologic
posts: 9
Registration: 21/07/20, 10:04

Re: Malne sanitary saunier duval thema c23E




by danpel » 21/07/20, 17:22

Hello, I don't see any part listed as a sensor on the boiler part plans and no part that looks like the one you present?
For the water valve, you can see it on the following link
https://www.esc-grossiste.fr/boutique/s ... -23-e.html
0 x
Christophe
Moderator
Moderator
posts: 79118
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10973

Re: Malne sanitary saunier duval thema c23E




by Christophe » 21/07/20, 17:51

Well there is necessarily a DHW flow detector ... do you have the instructions in .pdf? If so put it here as an attachment that we have a look at ...
0 x
danpel
I discovered econologic
I discovered econologic
posts: 9
Registration: 21/07/20, 10:04

Re: Malne sanitary saunier duval thema c23E




by danpel » 21/07/20, 17:54

I did not find any detector as explained, here is the file and thank you for your help
Attachments
ThemaC23E.pdf
(1.47 million) Downloaded times 652
0 x
phil59
Econologue expert
Econologue expert
posts: 2212
Registration: 09/02/20, 10:42
x 504

Re: Malne sanitary saunier duval thema c23E




by phil59 » 21/07/20, 18:00

Three-way valve HS?
0 x
hmmmmm, hmmmmmmmmmmmmm, hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhmmmmmmmmm, huh, hmmmmmmmmmmmmm.

: Oops: : Cry: :( : Shock:
danpel
I discovered econologic
I discovered econologic
posts: 9
Registration: 21/07/20, 10:04

Re: Malne sanitary saunier duval thema c23E




by danpel » 21/07/20, 18:05

I do not see a 3-way valve on the assembly drawing and neither at the supplier for this model of boiler
0 x
phil59
Econologue expert
Econologue expert
posts: 2212
Registration: 09/02/20, 10:42
x 504

Re: Malne sanitary saunier duval thema c23E




by phil59 » 21/07/20, 18:08

Indeed, maybe see P1, sanitary thermostat, can it bypass, to see what happens? (penultimate page of the pdf)
0 x
hmmmmm, hmmmmmmmmmmmmm, hhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhhmmmmmmmmm, huh, hmmmmmmmmmmmmm.

: Oops: : Cry: :( : Shock:
Christophe
Moderator
Moderator
posts: 79118
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 10973

Re: Malne sanitary saunier duval thema c23E




by Christophe » 21/07/20, 18:14

danpel wrote:I did not find any detector as explained, here is the file and thank you for your help


Ah yes I do believe that it is the water valve which fulfills this role: a membrane detects the pressure difference and regulates the gas flow.

Are you sure the valve that was changed is working?

If not yes also checks the DHW thermostat?