Bathroom Insulation (Thermal Bridge and Condensation)

Heating, insulation, ventilation, VMC, cooling ... short thermal comfort. Insulation, wood energy, heat pumps but also electricity, gas or oil, VMC ... Help in choosing and implementation, problem solving, optimization, tips and tricks ...
Melkior
I discovered econologic
I discovered econologic
posts: 7
Registration: 03/11/13, 12:07




by Melkior » 04/11/13, 21:34

Image


The aerator in question is on this photo, there is an identical one which extracts from the kitchen towards the bathroom placed on the opposite wall.

Image

Since the hot air is always high, and it makes a practically direct circuit from one wall to the other, that is to say a direct breath on the false ceiling cooled by the metallic structure which is in contact with the walls outside (cold).
Hence the traces of humidity on the areas bordering the metal structure.

Image

Not being at all professional can you help me by validating or denigrating this theory?


Thank you in advance
0 x
Melkior
I discovered econologic
I discovered econologic
posts: 7
Registration: 03/11/13, 12:07




by Melkior » 09/11/13, 00:24

I come back to the news, finally after dismantling all the false ceiling last Saturday, all of it has dried!
More humidity! in the end it was condensation in the false ceiling that caused all this damage!

By spanking a more precise inspection under the shower tray, I noticed a strong condensation ... have you ever been faced with that?
Is there a walkthrough?
0 x

 