Hello
I am surprised that you last 4 hours with 1500L of 80 to 50 ° C for 160m² ... because for convenience I have 200m² I have a 800L balloon and I go from 85 to 55 ° C in 5 hours or 26.5kWh or 5,3kWh. Hour ... DHW included ... at outside 0 ° C
I think you should review your insulation ...
Per cubic meter I need about 9.6Wh.m3 or 4 times less than normal (40Wh.m3)
In this case it is 32.5Wh.m3 so review your insulation and above all insulate all the heating pipes.
A+