a) Assembly (always on the "suction" side of the circulator)

b) Setting the network service pressure and vase


explanations:
P0 = Static pressure = height of your circuit m / 10 0.2 + b (the delta = 2 0 other in the case of an individual boiler installation)
PF = water pressure + cold = P0 bars at least 0.3
PSV = opening pressure of the safety group
Pe = final set pressure.
Example: a circuit 12 m high.
P0 vase = 12 / 10 + = 0.2 1.4 bar (usually set to 1.5 original bars)
PF cold water = 1.4 0.3 + = 1.7 bar
PSV = 3 bars (value in most cases, often not adjustable factory)
Pe of hot water = <2.5 bars (to be checked after increase in T °)
So the rule is to de / inflate the vase to the calculated value and add 0.3 bars on the water system. Then check to warm the value remains below safe pressure - 0.5 bars.
ps: hey this little free app looks nice
Reflex - free software offer
Software
calculation program for systems
exchangers and pressure maintenance
(Version 4.1.9) incl. 2006 rate
Reflex 4 (26.2 MB)
http://www.reflex.de/reflex/html/index.php?lang=10&tp=9
.pdf Version: https://www.econologie.com/vase-d-expans ... -4208.html