Hi,
To calm the temperature rise of the boiler, why not lower the value of the parameter P222 of the boiler regulation.
If I understand correctly the boiler temperature is controlled via the modulation, which controls the feed screw.
So if we put less fuel = less rapid temperature rise.
or maybe increase the parameter P223, break time of the screw?
Operating time boiler OKOFEN
Hello,
Thanks for the recommendations for P222 and P223.
After observations of the behavior of my boiler, I have some questions:
1-I noticed that I had + or - 5 ° difference between the temperature measurement displayed on the boiler control (P105) and boiler temperature measurement displayed on the Pelletronic (white regulator). Knowing that it is still P105 which is inferior to the Pelletronic measurement, normal?
2-When the v3v appears closed (visually), it still receives closing pulses. Normal or calibration problem of v3v?
3-What is the "action" of settings P265 on the boiler? electronic boiler clamping?
4- On an 15Kw boiler, how far can we go down on the parameter P265?
Thanks for the recommendations for P222 and P223.
After observations of the behavior of my boiler, I have some questions:
1-I noticed that I had + or - 5 ° difference between the temperature measurement displayed on the boiler control (P105) and boiler temperature measurement displayed on the Pelletronic (white regulator). Knowing that it is still P105 which is inferior to the Pelletronic measurement, normal?
2-When the v3v appears closed (visually), it still receives closing pulses. Normal or calibration problem of v3v?
3-What is the "action" of settings P265 on the boiler? electronic boiler clamping?
4- On an 15Kw boiler, how far can we go down on the parameter P265?
0 x
1- having 5 ° difference between the PLC measurement and the measurement is not very normal normal but not necessarily very embarrassing. as far as the PLC value is lower, it means that when the boiler restarts, the regulator thinks that it is still 5 ° above and it avoids cutting the V3V.
on the other hand if you are in P170 = 0, it is the regulator who decides when to cut the burner and thus cuts it 5 ° too early.
in short, you could take advantage of this problem with a P170 = 1 ... unless there is another thing that I did not think.
the other solution is to make the two values coincide as much as possible. a possible reason for the deviation is the way the probe is in mechanical contact with the boiler body.
you raise the thermal protection a little by following the wire of the probes and you will find small angles welded on the body of boiler. in these angles are inserted the 2 probes. try to improve the contact by sliding a small wedge between the probe and the angle. you can also add if you have some thermal paste that we put on electronic components.
2- it is normal for the pulse sending regul to close the V3V even when it is already closed. there is no position sensor in the V3V, the regul works blindly.
3- the P265 regulates the nominal power of the boiler, ie the couples: granule flow / air flow for the different modulation levels.
4- I do not know.
on the other hand if you are in P170 = 0, it is the regulator who decides when to cut the burner and thus cuts it 5 ° too early.
in short, you could take advantage of this problem with a P170 = 1 ... unless there is another thing that I did not think.
the other solution is to make the two values coincide as much as possible. a possible reason for the deviation is the way the probe is in mechanical contact with the boiler body.
you raise the thermal protection a little by following the wire of the probes and you will find small angles welded on the body of boiler. in these angles are inserted the 2 probes. try to improve the contact by sliding a small wedge between the probe and the angle. you can also add if you have some thermal paste that we put on electronic components.
2- it is normal for the pulse sending regul to close the V3V even when it is already closed. there is no position sensor in the V3V, the regul works blindly.
3- the P265 regulates the nominal power of the boiler, ie the couples: granule flow / air flow for the different modulation levels.
4- I do not know.
0 x
zeralium wrote:4- On an 15Kw boiler, how far can we go down on the parameter P265?
A difference of 2 kW is tolerated between the "physical assembly" [number of heat exchanger tubes condemned, therefore number of tubes remaining "open"] and the computer settings.
So a "physical" 15kw can be electronically restricted to 13kW without big performance losses.
0 x
Pradon: a doubt !!!
The P265 (I do not have the notice under the eyes), it is:
- the power ?
- the "nominal temp" ???
I answered for the power.
For temp nominal, if it is it, it is a very sensitive parameter! You drop 1 or 2 ° ... and it changes a lot!
Basically, very quickly, your boiler will "drag out", always modulating very very low, so it will be difficult to keep up with demand! Suddenly, you will very often have the V3V closed by the "anti-condensation" system and ... cold!
Start by lowering 1 and see if you are still in the wall [maximum temperature of the boiler reached very quickly, resulting in the start of the shutdown procedure!)
The P265 (I do not have the notice under the eyes), it is:
- the power ?
- the "nominal temp" ???
I answered for the power.
For temp nominal, if it is it, it is a very sensitive parameter! You drop 1 or 2 ° ... and it changes a lot!
Basically, very quickly, your boiler will "drag out", always modulating very very low, so it will be difficult to keep up with demand! Suddenly, you will very often have the V3V closed by the "anti-condensation" system and ... cold!
Start by lowering 1 and see if you are still in the wall [maximum temperature of the boiler reached very quickly, resulting in the start of the shutdown procedure!)
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 15 Replies
- 1178 views
-
Last message by sicetaitsimple
View the latest post
21/02/24, 19:34A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 0 Replies
- 3705 views
-
Last message by Stanley57
View the latest post
08/02/19, 21:21A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 5 Replies
- 4515 views
-
Last message by Did67
View the latest post
04/04/18, 12:03A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 10 Replies
- 8883 views
-
Last message by mooky
View the latest post
15/02/10, 22:54A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 0 Replies
- 2924 views
-
Last message by recyclinage
View the latest post
19/06/09, 21:46A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : Google Adsense [Bot] and 501 guests