I replaced the 3.6 V lithium battery which was soldered on the card (and which displayed 0.6 V.) with a box with 3 AA ni-mh batteries. At nominal voltage it is 3.6 V. (4 V. at measurement).
But it does not work
Nothing is displayed, and all relays remain open.
Anyone know this kind of bug
Question:
In auto mode, the boiler works above 60 °.
In manual mode I set it to 50 ° t ° of DHW.
During efficiency measurements made by the chimney sweep and by the maintenance service, the measured (calculated) efficiency is always better when the boiler is less hot (between 5% to 8% of losses).
Why does autopilot keep the boiler at a higher temperature than that required for hot water production
Heating and Insulation of an old building
-
- Grand Econologue
- posts: 1111
- Registration: 10/10/13, 16:30
- Location: Geneva countryside
- x 189
I will try to develop the ideas that germinated.
To put a gas burner in my current boiler does not seem to me judicious, I prefer a condensing boiler.
In another room, on the other side of the wall, I have a gas pipe installed and a flue, which dates from an old gas water heater.
It is outside the boiler room, I can install a gas boiler of 19 kW max. It is much cheaper than installing a more powerful gas boiler in the boiler room.
Instead of the current boiler, can I install a 15 kW pellet boiler, with either storage in the adjoining room with a worm screw, or outside with gravity feed?
In my living room fireplace, which is currently out of use, I install a hydro stove with logs, like an Alpenofen which sends 4.5 kW into the water, it is an exchanger with 1 inch steel outlets. It is just above the boiler, there is only the floor to cross.
On the roof, exposed S, SE, solar panels with a buffer (1500 l for starters ..?) Which will be placed next to the boiler, pile pile below the chimney. It remains to make the plan of the whole ...
There I will need your lights, because my antique installation has the advantage of having been designed in thermosiphon, the circulator was added after.
The sections are big, 3/4 "for the radiators, so it circulates well and the water leaving the boiler rarely exceeds 50 ° (in my grandfather's time, it was 45 ° maximum, now people have become cozy ...).
Now I have a question:
I read and understood all the advantages of a system of solar panels with emptying and automatic filling, and today even I was presented with a quote, with 140 liters of antifreeze ...
In self-draining panels, what is circulating? closed circuit water? water from an existing circuit? how do you get the air out?
So what do you think of my plan?
Complex, but I can use existing infrastructure.
Oversized (19 + 15 + 4)> 35
but I can turn without gas or without pellets
In addition, I will replace 40 m2 of glass, so save around 100 W / K. On very cold days, delta t 25 °, it is 2.5 kW less for birds.
To put a gas burner in my current boiler does not seem to me judicious, I prefer a condensing boiler.
In another room, on the other side of the wall, I have a gas pipe installed and a flue, which dates from an old gas water heater.
It is outside the boiler room, I can install a gas boiler of 19 kW max. It is much cheaper than installing a more powerful gas boiler in the boiler room.
Instead of the current boiler, can I install a 15 kW pellet boiler, with either storage in the adjoining room with a worm screw, or outside with gravity feed?
In my living room fireplace, which is currently out of use, I install a hydro stove with logs, like an Alpenofen which sends 4.5 kW into the water, it is an exchanger with 1 inch steel outlets. It is just above the boiler, there is only the floor to cross.
On the roof, exposed S, SE, solar panels with a buffer (1500 l for starters ..?) Which will be placed next to the boiler, pile pile below the chimney. It remains to make the plan of the whole ...
There I will need your lights, because my antique installation has the advantage of having been designed in thermosiphon, the circulator was added after.
The sections are big, 3/4 "for the radiators, so it circulates well and the water leaving the boiler rarely exceeds 50 ° (in my grandfather's time, it was 45 ° maximum, now people have become cozy ...).
Now I have a question:
I read and understood all the advantages of a system of solar panels with emptying and automatic filling, and today even I was presented with a quote, with 140 liters of antifreeze ...
In self-draining panels, what is circulating? closed circuit water? water from an existing circuit? how do you get the air out?
So what do you think of my plan?
Complex, but I can use existing infrastructure.
Oversized (19 + 15 + 4)> 35
but I can turn without gas or without pellets
In addition, I will replace 40 m2 of glass, so save around 100 W / K. On very cold days, delta t 25 °, it is 2.5 kW less for birds.
0 x
-
- Grand Econologue
- posts: 1111
- Registration: 10/10/13, 16:30
- Location: Geneva countryside
- x 189
Hello,
I haven't written anything since, because I haven't started yet ...
I still understood a little better how my boiler works, because I continue to adjust it manually. I get up before the others to go up the temperature .
I calibrated the ntc probe of the water heater in a pan, and I make readings on different heights (1.25m. At the bottom).
In the afternoon, and possibly. in the middle of the night, when the temp at -90cm arrives at 25 ° (47 ° at the top) I half close the v4v and I switch on the DHW circulator and raise the boiler to 60 °. After about 1 hour the DHW arrives at 55 ° over the entire height and I return to heating mode with the boiler at approximately 45 ° and the v4v fully open.
Today I reconnected the DHW pump when the DHW temperature = heating temperature, will we see if that is enough?
I also did an on-off reading in heating mode but 50 ° boiler / 45 ° heating. (v4v to 3/4), t ° ext -2 °, t ° int 17 °
Run 4 min 20 ", stop 2 min 20" ... I would prefer a longer cycle.
that's 65% of usage time for 35kW, so 22 kW of average power (without DHW).
These last two weeks I have consumed 400l. fuel oil.
I expose all these figures here to find them, I will try to group them later, I also make daily measurements of the walls and windows int-ext to be able to compare afterwards.
A+
Ps: the 120 liters that this energy-intensive building burned in 000 years, a 18-seat airbus burns them in 400 hours ...
I haven't written anything since, because I haven't started yet ...
I still understood a little better how my boiler works, because I continue to adjust it manually. I get up before the others to go up the temperature .
I calibrated the ntc probe of the water heater in a pan, and I make readings on different heights (1.25m. At the bottom).
In the afternoon, and possibly. in the middle of the night, when the temp at -90cm arrives at 25 ° (47 ° at the top) I half close the v4v and I switch on the DHW circulator and raise the boiler to 60 °. After about 1 hour the DHW arrives at 55 ° over the entire height and I return to heating mode with the boiler at approximately 45 ° and the v4v fully open.
Today I reconnected the DHW pump when the DHW temperature = heating temperature, will we see if that is enough?
I also did an on-off reading in heating mode but 50 ° boiler / 45 ° heating. (v4v to 3/4), t ° ext -2 °, t ° int 17 °
Run 4 min 20 ", stop 2 min 20" ... I would prefer a longer cycle.
that's 65% of usage time for 35kW, so 22 kW of average power (without DHW).
These last two weeks I have consumed 400l. fuel oil.
I expose all these figures here to find them, I will try to group them later, I also make daily measurements of the walls and windows int-ext to be able to compare afterwards.
A+
Ps: the 120 liters that this energy-intensive building burned in 000 years, a 18-seat airbus burns them in 400 hours ...
0 x
-
- Grand Econologue
- posts: 1111
- Registration: 10/10/13, 16:30
- Location: Geneva countryside
- x 189
Hello,
Here are some pictures to color the subject,
NE facade
NO facade
SE facade
SO facade
End of the roof
Detail of a radiator, I measured the temperature of the exterior wall with or without a reflector:
External wall (far from the radiator) 0 °,
outside temperature behind 4 ° radiator,
outside temperature with 2.3 ° reflector,
outside wall temperature with 3cm roofmat + 1.8 ° reflector.
My workshop, I have 10 meters to walk to work
A+
Here are some pictures to color the subject,
NE facade
NO facade
SE facade
SO facade
End of the roof
Detail of a radiator, I measured the temperature of the exterior wall with or without a reflector:
External wall (far from the radiator) 0 °,
outside temperature behind 4 ° radiator,
outside temperature with 2.3 ° reflector,
outside wall temperature with 3cm roofmat + 1.8 ° reflector.
My workshop, I have 10 meters to walk to work
A+
0 x
-
- Grand Econologue
- posts: 1111
- Registration: 10/10/13, 16:30
- Location: Geneva countryside
- x 189
Hi,
I found this link which seems interesting to calculate the heat loss of a wall.
http://calculis.net/resistance-thermique#resultat
I made a spreadsheet, with a ladle, and I arrive at the same result as my fuel oil consumption ...
I forgot the verandas, I need to refine the measurements of the facades.
A+
I found this link which seems interesting to calculate the heat loss of a wall.
http://calculis.net/resistance-thermique#resultat
I made a spreadsheet, with a ladle, and I arrive at the same result as my fuel oil consumption ...
I forgot the verandas, I need to refine the measurements of the facades.
A+
0 x
-
- Grand Econologue
- posts: 1111
- Registration: 10/10/13, 16:30
- Location: Geneva countryside
- x 189
Hello everyone,
I did a separate topic about the solar part,
right here: https://www.econologie.com/forums/post267622.html#267622
I continue here on the heating side, I made a schematic diagram.
With DIA, thank you forum, I do not master yet but it will come, I hope.
By the way, what tool do you use to make lines (pipes) and jumps of tubes?
The gas boiler has its own circulator.
The 4-way mixing valves are in principle not 100% waterproof, my boiler in summer works closed v4v to make the DHW and its expansion passes through the v4v.
For the buffer, given the volume, a minimum passage or a bypass is required, for operation in summer (solar storage).
I did a separate topic about the solar part,
right here: https://www.econologie.com/forums/post267622.html#267622
I continue here on the heating side, I made a schematic diagram.
With DIA, thank you forum, I do not master yet but it will come, I hope.
By the way, what tool do you use to make lines (pipes) and jumps of tubes?
The gas boiler has its own circulator.
The 4-way mixing valves are in principle not 100% waterproof, my boiler in summer works closed v4v to make the DHW and its expansion passes through the v4v.
For the buffer, given the volume, a minimum passage or a bypass is required, for operation in summer (solar storage).
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 3 Replies
- 1082 views
-
Last message by Lanig22
View the latest post
10/03/24, 18:51A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 8 Replies
- 1885 views
-
Last message by Ahmed
View the latest post
16/02/23, 11:19A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 25 Replies
- 5483 views
-
Last message by Christophe
View the latest post
03/12/22, 10:50A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 20 Replies
- 7547 views
-
Last message by Seb57
View the latest post
22/11/22, 10:19A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 4 Replies
- 1870 views
-
Last message by phil59
View the latest post
26/09/22, 19:31A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : No registered users and 403 guests