by Chris_Workshop » 30/07/19, 17:24
I have already done some calculations.
Regarding the amount of water and its location, it is impossible for it to be heated by the contribution of heat that will be pumped by the radiator.
The temperature of the water will not increase or it will increase infinitesimally. It takes 1 calorie to raise the temperature of 1 gram of water of 1 ° C and 1 calorie = 4,18 joules.
There is 20000 liters of water in the tank. so 2x10 power 7 grams of water. Therefore it takes 83,6 mega joules to raise these 20m3 1 ° C water. That is the equivalent of 23,2 kW.h. This means that it would be necessary to provide a power of 23,2 kW during 1h to raise the temperature of 1 ° C in the tank assuming that it is perfectly isolated. But this reserve is in contact with a surface of 32,5m² of concrete. himself in contact with the ground up to a depth of 5m. So even with such power we would not be able to heat this water in reality.
After the radiator will be far from being able to provide such a thermal power. As far as I'm concerned, I rely on an estimate from the small 7000 BTU air freshener I have at the moment. The air coming out is cooled to 15 ° C precisely. But clearly my system will be very superior. Already the radiator exchange surface of 306 is almost 6x higher than that of the cooler (665x350mm against 220x180mm is 2325cm² against 396cm²). In addition the blower part of the cooler does not break 3 paws to a duck. The 2 306 fan coils clearly stir more air, but then much more. While you hardly feel the breath of the cooler at 1m, you have hair in the wind at the same distance from the fans. So the top I'm quiet.
Another advantage over the cooler, the window will be closed while he needs it to be open to pass the hot air exhaust pipe and to introduce air to compensate for the air coming out of this pipe . Just that, it greatly hampers the performance of the cooler. My system will work all windows closed so.
In spite of all this small cooler of which I speak happens to make pass the temperature of a room of 22m ² of 31 ° C to 27 ° C in 4h. Not so bad. It is given for 7000 BTU (walnut unit which I do not control but which would be equivalent to 0,293W). So a priori but without warranty 7000 BTU correspond to 2051W. Maybe experts will give us details on it. Meanwhile I expect that my system will be at least as good as this little cooler. Therefore if it sends 2kW thermal in the tank it is not near to warm the water that it contains as demonstrated above. These 2000W will be easily distributed in the surrounding soil.
The flow rate of the P 0 delta pump is 1600l / h. Since the rising water column that goes to the radiator will make the same weight as the one going down into the tank we are at delta P 0. Since there will be losses due to pipes and other shrinkage I expect 1200l / h. Either a water velocity in pipes Ø15mm of 1,9m / s approximately. With such a speed, such a flow, there is no need for the pipes to be isolated. They will be cold all the time. And even if it's only half, in reality it will not change anything.
So even if it is not tested in real conditions we can not be completely sure, there is still little suspense in the success of this system.