My heat curve looks good on my pellet boiler when the weather is dry. On the other hand, as soon as the rain arrives, I have the impression that it is no longer "strong" enough to give me 19 °: Is this normal?
Thank you for your feedback.
Philippe.
Heating curve in wet weather
-
- I learn econologic
- posts: 39
- Registration: 01/03/18, 14:49
Re: Heating curve in wet weather
the heating slope does not have much to do with humidity.
the thermal losses of a building are proportional to the temperature difference between interior and exterior in first approximation.
a little raised in case of winds but humidity, I do not see.
however, thermal comfort is a function of humidity.
the thermal losses of a building are proportional to the temperature difference between interior and exterior in first approximation.
a little raised in case of winds but humidity, I do not see.
however, thermal comfort is a function of humidity.
0 x
-
- I learn econologic
- posts: 39
- Registration: 01/03/18, 14:49
Re: Heating curve in wet weather
Ah yes Dirk precisely the wind accompanies the rain very often at home ... So it can lower the inner T ° with the same heating curve?
0 x
Re: Heating curve in wet weather
It is possible that the wet walls increase (a little) the thermal losses compared to dry walls (on the windows, the effect is sensitive).Dirk Pitt wrote:a little raised in case of winds but humidity, I do not see.
Yes, without a doubt.Phil532140 wrote:Ah yes Dirk precisely the wind accompanies the rain very often at home ... So it can lower the inner T ° with the same heating curve?
The only way to ensure a constant temperature in any outdoor conditions is the indoor thermostat associated with a boiler (a little) more powerful than necessary.
The other methods (external probes, heating curve, ...) make it possible to minimize the consumption but at the price of approximation in the regulation of the interior temperature.
0 x
Re: Heating curve in wet weather
Gaston wrote:The only way to ensure a constant temperature in any outdoor conditions is the indoor thermostat associated with a boiler (a little) more powerful than necessary.
The other methods (external probes, heating curve, ...) make it possible to minimize the consumption but at the price of approximation in the regulation of the interior temperature.
Precision: the power has influence only on the speed of rise in temperature in the house except known under-sizing which is very very rare.
to make a talking image: the house is a pierced bucket that the boiler maintains at a certain level of filling.
in most cases, except very cold and very poorly insulated house, the power of the boiler is sufficient to maintain a "level" in the pierced bucket. on the other hand it can be more or less fast to reach this level if you come from a lower level (reduced at night for example)
the indoor thermostat would be like a level probe.
on a regulation with external probe, it is necessary to think well to regulate the coefficient of influence of the INNER probe.
[edit: Did67 to fix a quote tag. No change of text]
1 x
Re: Heating curve in wet weather
1) If the drop in comfort is significant when there is wind, one has to wonder about "leaks" by drafts (badly jointed frames?).
It may be added that for example walls exposed west, struck by the rain, are colder on the surface by evaporation of water. The fact that the external probe, placed in the dry, generally in the north, does not perceive either.
These two additional sources of losses put the regulation in the cabbages, because it always calculates on the basis of the only data which it has, the temperature recorded in the north and the dry one!
2) Indeed, the external sensor does not perceive these additional leaks and does not correct the resulting drop in temp.
3) Hence the interest, in addition, to have an internal room sensor, which "corrects" the observed deviation.
To take again the metaphor of the leaking bucket, the phenomena indicated in 1 ° enlarge the hole, thus the leaks, but the system does not know it, and pump always the same calculated quantity of water: the level drops!
It may be added that for example walls exposed west, struck by the rain, are colder on the surface by evaporation of water. The fact that the external probe, placed in the dry, generally in the north, does not perceive either.
These two additional sources of losses put the regulation in the cabbages, because it always calculates on the basis of the only data which it has, the temperature recorded in the north and the dry one!
2) Indeed, the external sensor does not perceive these additional leaks and does not correct the resulting drop in temp.
3) Hence the interest, in addition, to have an internal room sensor, which "corrects" the observed deviation.
To take again the metaphor of the leaking bucket, the phenomena indicated in 1 ° enlarge the hole, thus the leaks, but the system does not know it, and pump always the same calculated quantity of water: the level drops!
2 x
-
- Similar topics
- Replies
- views
- Last message
-
- 1 Replies
- 2875 views
-
Last message by yves67
View the latest post
27/11/22, 11:29A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 5 Replies
- 2875 views
-
Last message by Pilpoill
View the latest post
18/11/21, 20:45A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 81 Replies
- 81858 views
-
Last message by stef1
View the latest post
12/12/15, 18:09A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 114 Replies
- 75004 views
-
Last message by dhaulagiri
View the latest post
23/02/11, 14:58A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 0 Replies
- 1996 views
-
Last message by Xian
View the latest post
15/02/09, 15:29A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : Majestic-12 [Bot] and 261 guests