Mic74 wrote:Here is the photo of this morning (in the place!), The set flow temperature was 26, and the temperature measured by the 46 regulation.
This photo is intriguing and may suggest that your V3V is upside down (including the color rim)
- We are in the blue, an almost closed V3V: theoretically, especially is sent back from the water, with almost no hot water from the boiler ...
- Or the start is almost 60, a few degrees below the temperature of the boiler (between 65 and 75)
- the return is much lower than the departure; it "turns" in the right direction ...
- With a reference to 26, ever in life you do should have a circuit at those temperatures
The first thing I would do would be to remove the engine and drive the V3V by hand, to see if everything works: you dismantle the block, and you put your V3V on an "average" position [you heat with radiators?]