See assembly here: https://www.econologie.com/forums/chaudiere- ... t4589.html
How did I do? Very easily: I closed all the other valves except those of the DHW tank and I measured the T ° before / during / after.
Thus the only energy, apart from the "losses" in the pipes and at the level of the boiler, is that which will heat the sanitary water. Obviously I had turned off the hot water during these measurements.
Then we bring everything in kWh (or other) and the effective output is given by: "energy supplied to the DHW tank / energy contained in the fuel"

Measurement protocol:
- boiler start off
- weighing the mass of wood (= fuel load)
- the T ° of the DHW tank is periodically noted (every 1 hour)
- For the initial and final T ° we take the T ° between 2 measurement point (stratification in the flask)
- "Full" draft all the time (turbo draft plate turned upside down) and continuous circulator (power 65W)
Data and results:
- Initial tank temperature: 31.5 ° C
- Final tank temperature: 50.5 ° C
- Tank volume: 300L or energy to raise the tank by 1 ° C: 0,35 kWh (= 300 * 4.18 / 3600)
- Energy "gained" by the balloon: (50.5-31.5) * 0.35 = 6.65 kWh
- Fuel load: 7,9 kg, burnt mass estimated at 7 kg.
- PCI wood: 4 kWh / kg (probably a little more, compressed sawdust of oak or exotic wood)
- Energy "burned" by the boiler: 7 * 4 = 28 kWh
Yield (miserable) of: 6.65 / 28 = 24% !!!


I found that beyond 45 ° C the boiler had great difficulty in heating. The best (quickest) rise in T ° was between 35 and 45 ° C (tank temperature). The maximum power recovered by the DHW and averaged over one hour was 2.1 kW (boiler given for 13 to 15kW but the fuel load was not maximum I grant you!)!
Here is the diagram of the assembly:

I don't think this is the deom boiler assembly which is mediocre (we have already discussed it a lot) but the capacity of the boiler to recover calories. Obviously there are some losses in the non-insulated pipe.
Once again we see the difference between a REAL yield and a "laboratory" yield under ideal conditions (the Deoms are given for 65 to 70% yield !!!).
Are some of you ready to do the same manipulation on your wood boiler (or fuel oil, possibly with a container?)? I would like to have the actual effective output of an ökofen boiler for example. For fuel oil I could possibly do it myself as soon as the repair of ours is finished.
For my part I would do a test by changing the parameter: automatic mode (with comparator) for the circulator and draft regulated by the valve integrated in the boiler. I thus hope to be able to go up to 50% effective return. Beyond that I no longer believe in it too much.
ps: the test was carried out after the sweeping mentioned here https://www.econologie.com/forums/eviter-le- ... t6976.html