Hello
We have just acquired a property with an okofen pellematic PE 8-56 boiler, we start it but the radiators do not heat up ....
The previous owners did not send us the information after wintering.
Can you help us?
Thank you in advance
voyageuse
Okofen Pellematic PE 8-56
Re: Okofe pellematic
Sorry for the mistakes, after starting up no heating in the radiators
Should we open a water valve?
Should we open a water valve?
0 x
-
- Moderator
- posts: 79323
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11042
Re: Okofen Pellematic PE 8-56
Hi and welcome here.
The circulator (s) rotate?
After a few months (see weeks) of non-use, circulators are often seized.
They must be unclipped by opening the central nut and turning the screw by hand a few turns with a screwdriver. Next seizure is more or less easy. Some use a hammer to give a few strokes in the direction of the motor axis and it works (banging with small strokes).
Obviously this must be done when the boiler is off.
The circulator (s) rotate?
After a few months (see weeks) of non-use, circulators are often seized.
They must be unclipped by opening the central nut and turning the screw by hand a few turns with a screwdriver. Next seizure is more or less easy. Some use a hammer to give a few strokes in the direction of the motor axis and it works (banging with small strokes).
Obviously this must be done when the boiler is off.
0 x
Do a image search or an text search - Netiquette of forum
Re: Okofen Pellematic PE 8-56
There are several kinds of regulation, depending on the years of manufacture.
If you could tell us what regulation is the boiler equipped with? Or a photo of the "screens" ???
It may be in "summer" mode and only heat hot water ... Or "frost protection" - and only chuaffe if the temperature drops below 8 ° C ... Etc ...
It is a very good boiler, but with a little complex regulations ...
If you could tell us what regulation is the boiler equipped with? Or a photo of the "screens" ???
It may be in "summer" mode and only heat hot water ... Or "frost protection" - and only chuaffe if the temperature drops below 8 ° C ... Etc ...
It is a very good boiler, but with a little complex regulations ...
0 x
Re: Okofen Pellematic PE 8-56
Traveler wrote:Hello
We have just acquired a property with a boiler okofen pellematic PE 8-56
The appellation 8 - 56 intrigues me ... Is this what is written on the plate ???
0 x
-
- Moderator
- posts: 79323
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11042
Re: Okofen Pellematic PE 8-56
Already check if the circulators are running before anything else ... since the boiler was visibly "in wintering" ... (for me that means off ...)
0 x
Do a image search or an text search - Netiquette of forum
-
- Similar topics
- Replies
- views
- Last message
-
- 1 Replies
- 1141 views
-
Last message by Pilpoill
View the latest post
12/02/24, 22:04A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 11 Replies
- 2203 views
-
Last message by Pilpoill
View the latest post
15/12/23, 17:08A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 10 Replies
- 3200 views
-
Last message by Clemclem
View the latest post
26/12/23, 11:05A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 1 Replies
- 1180 views
-
Last message by sicetaitsimple
View the latest post
01/12/23, 21:27A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 2 Replies
- 2032 views
-
Last message by bighorno
View the latest post
15/12/23, 21:55A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : Google Adsense [Bot] and 498 guests