Tried what?
Izy, if the ECS-PAC circulator runs 24 hours a day, it is because I have increased the setting of the ECS thermostat since it is this one which controls (controlled?) its triggering...basically now the ECS thermostat is no longer useful , it's just the circulator switch: it's on max all the time...After analyzing the consumption and ambient temperature curves after a few days in this configuration I
a start every 2 hours for approximately 10 minutes of compressor operation (= 12 * 0.167 = 2h / day)...VS 4 starts per day of 25 to 30 min for the first 2 seasons...( = around 2h / day too...How strange is that!

)
But I consume a little more every day: gone from 1.2 to 1.3 kWh to 1.6 to 1.7 kWh...(+ 30%)
The circulator alone in minimum position (when the heat pump is not turning) is 0.01 * 22 = 0.22 kWh/day...before it consumed 0.03 * 2 = 0.06 kWh/day so the own consumption of the heat pump went from :
- Season 1 and 2: 1.25 - 0.06 = 1.2 kWh/day
- Season 3: 1.65 - 0.22 = 1.4 kWh/day
So the compressor runs a little more (+ 17% of the time) but for a slightly higher DHW temperature (improved comfort)...
On the other hand, if I put the DHW circulator at high speed in this configuration (which was the best setting for season 1 and 2), the daily consumption explodes to 2.5 kWh... (with 24 * 0.03 = 0.72 kWh of circulator consumption and 1.8 kWh consumption PAC)...
So the new configuration seems better to me but it creates more start-up cycles...Is this really annoying (= premature wear?) for a heat pump? A fridge must also start around ten times a day...
Well, still no one to do a similar montage?