Hello, I am looking for an opinion on my water heating system in thermosiphon that I made with recycle but that does not boot any more since I connected the cumulus.
here is a shema that represents everything:
Thermosyphon for water heater
-
- I discovered econologic
- posts: 3
- Registration: 12/12/14, 14:49
-
- Moderator
- posts: 79844
- Registration: 10/02/03, 14:06
- Location: Greenhouse planet
- x 11311
Re: Thermosyphon for water heater
Watch out for the air in the circuit that is plugging at the highest point.methabaron wrote:Hello, I am looking for an opinion on my water heating system in thermosiphon that I made with recycle but that does not boot any more since I connected the cumulus.
here is a shema that represents everything:
Make sure that the right part of the sensors is higher than the left part so that any bubbles that form in the sensors can rise along the hot pipe. Install the overflow at the top of the circuit so that air can escape.
0 x
-
- I discovered econologic
- posts: 3
- Registration: 12/12/14, 14:49
so do
Cuicui thank you for his advice, but everything is in order, the slopes, the air bubbles, and an overflow at the top of the circuit.
I wondered if the diameter of my pipes was enough?
and yes christophe it is a panel at the bottom.
I wondered if the diameter of my pipes was enough?
and yes christophe it is a panel at the bottom.
0 x
Ahmed wrote:if you can not / want to move the expansion tank / too full, you must place an automatic trap on the circuit, at the top of the balloon.
+1
As long as the circuit is not pressurized, the automatic high-point bleed can be replaced by a simple 6 mm tube that rises higher than the expansion tank.
In desperation, you can insert a circulator in the downstream collector and use it to start the circuit. A stationary circulator does not prevent the thermosiphon.
What is the diameter of your collectors?
0 x
Yes, the small diameter tube placed in the right place is a simple and effective solution *, especially as automatic purgers have an unfortunate propensity to get stuck and to have more "automatic" than the name **!
A stationary circulator does not prevent a thermosiphon from functioning, but if the load losses are already high, it is not certain that this small additional loss is not prohibitive ...
* It would be interesting to have an expansion tank.
** Even blocked, an automatic vent can still be operated by hand, but can also be replaced by a simple tap ...
A stationary circulator does not prevent a thermosiphon from functioning, but if the load losses are already high, it is not certain that this small additional loss is not prohibitive ...
* It would be interesting to have an expansion tank.
** Even blocked, an automatic vent can still be operated by hand, but can also be replaced by a simple tap ...
0 x
"Please don't believe what I'm telling you."
I guess it's in case the circuit is put under pressure?Ahmed wrote:Yes, the small diameter tube placed in the right place is a simple and effective solution.
It would be interesting to have an expansion tank.
Even blocked, an automatic drain can still be operated by hand, but can also be replaced by a simple tap ...
0 x
-
- Similar topics
- Replies
- views
- Last message
-
- 0 Replies
- 6702 views
-
Last message View termochauff
View the latest post
29/11/17, 14:01A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 7 Replies
- 13848 views
-
Last message View the middle
View the latest post
12/12/09, 08:56A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 5 Replies
- 99328 views
-
Last message View MJB61
View the latest post
04/10/23, 11:54A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
-
- 9 Replies
- 23539 views
-
Last message View Philippe Schutt
View the latest post
17/01/09, 23:05A subject posted in the forum : Heating, insulation, ventilation, VMC, cooling ...
Back to "Heating, insulation, ventilation, VMC, cooling ..."
Who is online ?
Users browsing this forum : No registered users and 407 guests