F5 corresponds to a compressor thermal shutdown (Klixon) difficult to understand after X months of shutdown so I had doubts about this self-diagnosis.
And when I tested on the thermal quick connector I had continuity!
I spent 2 days diagnosing the fault, tested all the other sensors, in particular calibrated the NTC probes (telling myself that the error codes are not 100% reliable?) to finally find it was a false contact in the connector quick of the klixon !
The thermal was good, the wires too but there was a bad contact with the connectors (1 or 2?) when it was plugged into the power board !
The continuity test is done on the side of the quick connectors, not on the pins.
So I removed this quick connector from m... and I made a direct connection to the power board... and mazel tov, it works again (for 10 years I hope!)...
In short, I spent 2 days to repair this breakdown instead of 15 minutes... the crazy breakdown! If it can benefit others...
I am convinced that a pro would have said, after 2 or 3 hours of hair-tearing diagnosis: power board dead, air conditioning to be changed!

In short, the error codes on the old air conditioning are a jungle, so here are the error codes that correspond to this old air conditioning (do not count on the Airton after-sales service, which is absolutely useless...)